Re: Surge protecting your network

Quote:
Originally Posted by APS View Post
The router power comes via way of a transient protected mains supply and a UPS, so I am pretty sure the surge may have come in via the VM cable.
First off, how do you know AC electric has any protection from that type of surge? If the UPS does protection, then post a UPS number that says so. Most UPSes have near zero protection. Just enough above zero so that a majority call it 100% protection.

If your AC has transient protection, then that device has a low impedance (ie 'less than 3 meter') connection to single point earth ground. Many transient protectors only claim to suppress noise. A destructive surge easily blows right through those devices.

Second, same applies to an earth ground for that VQ301. To be earthed means a low impedance (ie 'less than 3 meter') connection to earth. So we just pretend those centimeter parts will stop what three kilometers of sky could not.

A wall receptacle safety ground is called earth. An earth ground for protection is a metal plate or rod actually in earth. The two 'earths' are electrically different. Only share a common name. Connecting a VQ301 only to a safety ground means it is not earth, does not connect to a single point ground, and does not do surge protection. To be earthed for surge protection, a connection must be low impedance (ie 'less than 3 meters') to the same earth ground even used by the AC transient protector (that must also make a low impedance connection).

The isolator is doing what should alread exist in appliances - galvanic isolation at 2000 volts. It only provides major transient protection when the screw attaches a wire to a true earth ground.

Without a connection to earth that short, then the isolator can only block small transients. Duplicates (not improve) what should already exist inside each appliance. To make irreleavnt a destructive transient (which you apparently had), an isolator must connect that screw low impedance to a true earth ground.