Welshchris is the helpful oneWelshchris is the helpful oneWelshchris is the helpful oneWelshchris is the helpful oneWelshchris is the helpful oneWelshchris is the helpful oneWelshchris is the helpful oneWelshchris is the helpful oneWelshchris is the helpful oneWelshchris is the helpful oneWelshchris is the helpful oneWelshchris is the helpful oneWelshchris is the helpful oneWelshchris is the helpful oneWelshchris is the helpful oneWelshchris is the helpful oneWelshchris is the helpful oneWelshchris is the helpful one
Re: Economy 7 Immersion Heater Help.

Quote:
Originally Posted by raging bull View Post
Did they leave any of the instruction leaflets with you?
The heaters are a nominal 3Kw = 12 amps load
The thermostats are 15amp switching capacity
Unless they have picked a foreign make, that should have been o'k.
No idea, but they even fitted a stat in without a thermal cutout and it instantly died.

Well hopefully its done now.... 2 new elements and 3 new thermastats just got to wait till the morning now to see if the Econemy 7 Works.

I hope no one was listening by my door when the plumbers were draining the water... The drainage valve on the bottom wouldnt open so they had to drain from top of tank, u had one plumber by the tank and the other one in the bathroom sucking on a hose saying "This is discusting its hitting the back of my throat and gagging" and then u had the plumber by the tank saying COME ON SUCK IT SUCK IT!.