Quote:
|
Originally Posted by SMHarman
Then the risk is pretty minimal, the power is for the spark / clock. If you look, you may well find the 13A cable is permanently connected to the cooker, so the wiring is correct!
|
Okay, I'm confused now!

13 amp cable connected to the cooker. Where did that come from? Am I missing something?
If the 2.5mm2 cable is connected to the 6.0mm2 cable and protected by a 30 amp fuse or circuit breaker then either the wiring needs to change of the protection needs to be reduced to 16A. So the wiring is not really correct.