Mike is the helpful oneMike is the helpful oneMike is the helpful oneMike is the helpful oneMike is the helpful oneMike is the helpful oneMike is the helpful oneMike is the helpful oneMike is the helpful oneMike is the helpful oneMike is the helpful oneMike is the helpful oneMike is the helpful oneMike is the helpful oneMike is the helpful oneMike is the helpful oneMike is the helpful one
Re: Any electrician out there ?

Quote:
Originally Posted by abailey152
A cooker outlet usually consists of a 30 amp double-pole switch at high level and a connection unit lower down. Some cooker switch units have a socket outlet on them also (a socket outlet and a large switch marker Cooker). Have you got anything that resembles this? Or have you got a normal socket outlet?

Whether this is the JB or not depends how it was done. Somewhere there will be a joint where the 6.0mm2 cable is joined to a 2.5mm2 cable. It may well be a proper Joint Box.


Your cooker circuit is protected with a 30 amp fuse of circuit breaker. This is too large for a 2.5mm2 cable, so if you are running a standard socket outlet off this circuit, and assuming that the joint is okay (i.e. done in a proper safe manner), then the fuse or circuit breaker for this circuit needs reducing to 15 amp (16 amp for an MCB)


Thanks again
[/QUOTE]


I really apprecaite the advice...............want has happen is the house has had various electrical tests over the past 5 years becuase it is a rental house it has always passed but now it has failed because of the items. So do I presume at something someone had changed things for it to now fail.